Maybe I'm missing something here. GEC and ground rod wire are the same thing. Also, is this a POCO meter base, or a home depot meter base?Anyone see anything wrong in running both of these to meterbase? If so, could we polaris tap them to go into single meter lug?
Sent from my iPhone using Tapatalk
Anyone see anything wrong in running both of these to meterbase? If so, could we polaris tap them to go into single meter lug?
Sent from my iPhone using Tapatalk
Because the meter is sealed, we are not allowed to land any GEC conductors in it. That's a shame, because it's the perfect place to land the ground rod GEC.
Because the meter is sealed, we are not allowed to land any GEC conductors in it. That's a shame, because it's the perfect place to land the ground rod GEC.
NEC allows it. But not using a polaris to splice the GEC because the GEC has to be continuous. You could perhaps splice the neutral and bond the GEC to it using a polaris, as long as the GEC itself is not spliced there. Seems like there must be a better way than a polaris.
Usually around here the GEC is only landed at the meters if there are multiple meters, and then there's an extra lug for it.