GEC and meter base

Status
Not open for further replies.

ivsenroute

Senior Member
Location
Florida
Who connects the GEC to the meter base and who does not?

I am asking this question because there appears to be inconsistency amongst POCOs concerning this issue.

Here is an excerpt from one of the POCOs that service my area:

d. Installation of Grounding Electrode Conductor:
The grounding electrode conductor shall be installed directly between the grounding
electrode and the service disconnecting equipment and shall not pass through the
meter base or be connected to any grounding lug in the meter base.
 

480sparky

Senior Member
Location
Iowegia
We can't land the GEC in the meter either, which creates a vacuum. :mad:

That's all? Doing so here creates a black hole.
emoticon-0140-rofl.gif
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I have always made the GEC in the meter enclosure in residential services, it's the most logical place to make it. Why take a surge into the inside of a building?

Roger
 

ceb58

Senior Member
Location
Raeford, NC
I always land in the meter base. It has never been an issue with local poco's. But may I ask those that do not/ can not land in the meter base. Dose the poco provide the meter base?
 

480sparky

Senior Member
Location
Iowegia
I have always made the GEC in the meter enclosure in residential services, it's the most logical place to make it. Why take a surge into the inside of a building?

Roger

I recall something about 'first point of disconnect', which the meter is not.

250.64(D)(3) in the '08?
 

electricalperson

Senior Member
Location
massachusetts
i always land my GEC in the meter. our meter sockets are approved from nstar for that use. l put the number 6 awg from the rods to the meter and attach the ufer ground and water pipe to the panel
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I recall something about 'first point of disconnect', which the meter is not.

250.64(D)(3) in the '08?

It is only required to be made in a wireway or other accessible enclosure on the supply side of the disconnect.

A meter enclosure is accessible regardless of what some POCO's want us to believe, as a matter of fact, it is more accessible than being behind locked doors inside buildings or dwelling units.

Roger
 

480sparky

Senior Member
Location
Iowegia
It is only required to be made in a wireway or other accessible enclosure on the supply side of the disconnect.

A meter enclosure is accessible regardless of what some POCO's want us to believe, as a matter of fact, it is more accessible than being behind locked doors inside buildings or dwelling units.

Roger

But the POCO can make 'accessible' a real PITA.

ElectricMeterWithLockRing.jpg
 
For years we would have to wait for the POCO to show up to unlock the meter...sometimes that could be days or even weeks.

Then I bought a Dremel and the wait time dropped to less than 5 minutes. If the POCO complained, we would tell them there was "arcs and sparks", it was an emergency... ;):grin:
 