Looking for some clarification.
I have a 150kva transformer fed from 250cu on 225amp breaker for primary.
Secondary I have two sets of wires(not paralleled.)
One set is 250cu feeding 250amp main breaker panel
Second is 250cu feeding 200 amp main breaker panel.
Question 1) for sizing GEC I just take the largest ungrounded derived conductor (250cu)
Or do I treat them as a parallel and follow that for GEC sizing?
If I just follow largest ungrounded conductor for sizing, we get #2 cu for GEC.
The question arises if both secondaries fault, there is a potential for the ampacity of both 250cu and 250alum feeds.
Do I not think about the total ampacity of the transformer secondaries when sizing this and just look at the largest un grounded conductor?
I attached a picture to better describe my situation.
Thanks in advance for your input!
I have a 150kva transformer fed from 250cu on 225amp breaker for primary.
Secondary I have two sets of wires(not paralleled.)
One set is 250cu feeding 250amp main breaker panel
Second is 250cu feeding 200 amp main breaker panel.
Question 1) for sizing GEC I just take the largest ungrounded derived conductor (250cu)
Or do I treat them as a parallel and follow that for GEC sizing?
If I just follow largest ungrounded conductor for sizing, we get #2 cu for GEC.
The question arises if both secondaries fault, there is a potential for the ampacity of both 250cu and 250alum feeds.
Do I not think about the total ampacity of the transformer secondaries when sizing this and just look at the largest un grounded conductor?
I attached a picture to better describe my situation.
Thanks in advance for your input!