GEC at Fused disconnect for a Photovoltaic System

Merry Christmas
Location
Arizona
Occupation
Solar technician/electrician
Would a GEC at the fused disconnect be required for a photovoltaic system if we are bonded at the fused disconnect? This would be for a supply side tap the fused disconnect would be our overcurrent protection device. And if it is required to have a separate GEC at the fused disconnect what code is it referencing?


Sent from my iPhone using Tapatalk
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
If you are on the 2020 code see 250.25. And 250.64(D). The answer is probably yes, you need a GEC or a GEC tap, unless the neutral is ground at or upstream of the supply side tap.

But see also recent discussion here:

As I said in thread, IMO the PV disconnect should be treated as an additional service disconnect. But your mileage with your AHJ may vary.
 
Location
Arizona
Occupation
Solar technician/electrician
If you are on the 2020 code see 250.25. And 250.64(D). The answer is probably yes, you need a GEC or a GEC tap, unless the neutral is ground at or upstream of the supply side tap.

But see also recent discussion here:

As I said in thread, IMO the PV disconnect should be treated as an additional service disconnect. But your mileage with your AHJ may vary.

Thank you! This was very helpful.


Sent from my iPhone using Tapatalk
 