is it a violation to attach a GEC to a service disconnect by means of a mechanical lug to the enclosure exterior?

I have got two 100 amp disconnects that have no allowance to attach any more conductors to the factory neutral assembly inside.
Poco will not allow GEC to terminate in meter base that the disconnects feed from.

Rewiiring half of a duplex and found there was never a grounding electrode system installed when it was built in 1968.

Looking for a compliant fix without reworking the entire service.

thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Couldn't the GEC be connected directly to the neutral conductor in the disconnect?
 