From NEC 2020 Handbook via NFPAlink. 250.24(A)(1) - with Enhanced Content.
"
(1) General.
The grounding electrode conductor connection shall be made at any accessible point from the load end of the overhead service conductors, service drop, underground service conductors, or service lateral to, including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
Enhanced Content:
Allowing various connection locations meets the overall objectives for grounding while permitting a variety of practical options. The exhibit below illustrates three possible connection points where the GEC is permitted to be connected to the grounded service conductor. The accessibility to the point of connection has to be approved by the AHJ based on local conditions such as locked meter socket enclosures.
"