When a GEC, water bond, ect enters an enclosure, is it required to be bonded at the point of entry?
When a GEC, water bond, ect enters an enclosure, is it required to be bonded at the point of entry?
Forgetting what we think the NEC requires tell us why based on your engineering skills there may be a choke on a GEC through the bottom of an enclosure (maybe an 1/8") and the actual choke (or maybe Lenz law effect) of the same GEC through a ferrous metal "tube".When a GEC, water bond, ect enters an enclosure, is it required to be bonded at the point of entry?
What exactly is this "enclosure" you speak of? 250.64(E)(1) requires it, however I am not sure the intent is to require bonding the a cabinet as it enters. I think there was another thread on this very recently.
Meter can, main disconnect, electrical load center- the usual.
I take the enclosure in 250.64(E) to be a enclosure specifically for the GEC, not a more general enclosure like a cabinet, meter can, etc.
No matter the enclosure, if there are no splices in the box the GEC can pass through. It can be simply a pull point. Just my experience
Current active thread on basically same topic - http://forums.mikeholt.com/showthread.php?t=188549What exactly is this "enclosure" you speak of? 250.64(E)(1) requires it, however I am not sure the intent is to require bonding the a cabinet as it enters. I think there was another thread on this very recently.
Agreed, please respond at kwired's link.Current active thread on basically same topic - http://forums.mikeholt.com/showthread.php?t=188549