Electron_Sam78 Senior Member Location Palm Bay, FL Apr 25, 2010 #1 By code can I run a GEC through conduit that has other conductors in it? Last edited by a moderator: Apr 25, 2010
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 25, 2010 #2 I know of nothing that prohibits it. If the conduit is ferrous, 250.64(E) would be applicable.
Buck Parrish Senior Member Location NC & IN Apr 25, 2010 #3 Yes - Depending on the size and solid or standed