I know a lot of you have probally seen separtley derivie systems (transformers) have the Grounding Electrode Conductor (GEC) terminated on the outside casing of the xformer. Inside the Xo is bonded to the frame enclouser of the xformer.
I belive this is in contrast to the code.
In review the 2005 NEC250.24 it states that the GEC has to connect to the grounded service conductor or per 250.24 (4) ground terminal bus.
Also per the 8th edition of SCORES pg 71 Low Impedance GEC Connections it specifically notes that this connection has to be "within" the enclouser on the grounded service conductor.
Would connecting the GEC on the outside of the xformer with the XO bonded properly inside contrast he code?