Is the GEC connection to the main bonding jumper from the CEE considered accessible if it is in the sealed portion of the service entrance equipment?
Even if it were locked, I would still agree.mivey said:Since you can get to it without damaging the building structure or finish, I would say yes.
In my opinion, you are correct. :smile:A/A Fuel GTX said:Agreed.......So, if I have a multi position meter pack with NO tenant mains and NO main breaker, I can land my GEC to the neutral busing in the exterior service entrance section and not have to run the GEC to each of the interior load centers where my disconnects are?
Which is sad, because it's the ideal place to land it.boboelectric said:The reason we can"t connect the g.e.c. in the meter socket is the power company seals it shut,making it inaccessable
charlie said::-? However, I have never understood how this squares with 250.24(D)!?!
250.24(D) Grounding Electrode Conductor. A grounding electrode conductor shall be used to connect the equipment grounding conductors, the service-equipment enclosures, and, where the system is grounded, the grounded service conductor to the grounding electrode(s) required by Part III of this article. This conductor shall be sized in accordance with 250.66.
boboelectric said:The reason we can"t connect the g.e.c. in the meter socket is the power company seals it shut,making it inaccessable
infinity said:Around here the POCO explicitly forbids the connection to be within their equipment.
Yes.crossman said:. . . Is that what you are referring too?
Dennis Alwon said:I realize they have the power to do that but if I buy the meter base it isn't their equipment. Such bull. What harm does it do. Why would you ever need access to it. If you have to move the service or upgrade we cut the seal anyway. Seems like a power trip to me.