GEC connection

Status
Not open for further replies.

nizak

Senior Member
Does the GEC need to be brought to the main service disconnecting means first in order to comlpy with 250.24(A) (1)? Have a retro job where the GEC is currently run to a 300A main breaker panel which before was the first panel after the CT cabinet. Now a service disconnect has been added to the building exterior and that in turn feeds that first panel. Am I wrong in calling that panel now a sub panel? Not a big deal to change it just not sure if it needs to be. Thanks. FWIW this is a 120?240 Delta 3P system.
 
The gec needs to go to the service- usually the meter or the first disconnect.
 
Last edited by a moderator:
ahh i see. I have never worked with a 120/240 3 phase before. A 120/240 3 wire yes but not a 3 phase. 120/208Y i have worked with many times. It must be a older system ?? The delta stuff I dont have any experience with, yet.
 
ahh i see. I have never worked with a 120/240 3 phase before. A 120/240 3 wire yes but not a 3 phase. 120/208Y i have worked with many times. It must be a older system ?? The delta stuff I dont have any experience with, yet.

Yes 120/240 3 Phase Delta is an older system but is still very common in older shops. Beware of high leg when adding 120V circuitry. One of our guys took out 4 cash registers a few years ago when he landed a 120V receptcale circuit on the " stinger " phase.
 
The delta stuff I dont have any experience with, yet.
Just a quickie:

In a 240v Delta, the 120/240 section is exactly the same as a typical 120/240v 1ph service. The difference is that there is a third line conductor, which is 240v from each of the other two lines, and an unusable 208v from the neutral.

Think of it as a 120/240v 1ph service "superimposed" on a 240v 3ph Delta service. It's a simple triangular, or Delta, arrangement of three 240v transformer secondaries, and the center tap of one of them is the grounded neutral.
 