Drstuess
Member
- Location
- Narragansett, RI, USA
Hi folks,
Opened the service disconnect in attached garage for the first time. The GEC is just free in the enclosure and is not landed on the ground/ neutral bus. The GEC just exits the disconnect, goes through the wall and into the electrode in the ground. The neutral and ground from the house MLO (sub) panel in the basement are bonded together and to the enclosure at the disconnect (neutral is isolated in basement panel as it should be), but the enclosure is not bonded to the GEC. The meter, exterior wall of where the disconnect is mounted, has no grounding provision and only has the 3 conductors from the pole and (3) 4/0 SER into the disconnect. The GEC does not enter or bond with the meter enclosure at all.
My read is that this is simply not up to code, as the the neutral and "ground" are bonded at the appropriate location, however not actually grounded at the entrance in any of the 3 permitted locations. Bonding the GEC to the neutral/ ground bus in the disconnect should solve this... currently ~ .2 V between GEC and ground/Neutral bus in disconnect, showing no continuity. I know this is a basic situation and seems obviously out of code, but am I missing anything? Could the system be grounded up to code in some way I am not thinking off? -Water main is grounded and seems to have its own electrode on other side of the house, but appears to not be directly bonded with any electrical.
Appreciate the help and happy new year.
Opened the service disconnect in attached garage for the first time. The GEC is just free in the enclosure and is not landed on the ground/ neutral bus. The GEC just exits the disconnect, goes through the wall and into the electrode in the ground. The neutral and ground from the house MLO (sub) panel in the basement are bonded together and to the enclosure at the disconnect (neutral is isolated in basement panel as it should be), but the enclosure is not bonded to the GEC. The meter, exterior wall of where the disconnect is mounted, has no grounding provision and only has the 3 conductors from the pole and (3) 4/0 SER into the disconnect. The GEC does not enter or bond with the meter enclosure at all.
My read is that this is simply not up to code, as the the neutral and "ground" are bonded at the appropriate location, however not actually grounded at the entrance in any of the 3 permitted locations. Bonding the GEC to the neutral/ ground bus in the disconnect should solve this... currently ~ .2 V between GEC and ground/Neutral bus in disconnect, showing no continuity. I know this is a basic situation and seems obviously out of code, but am I missing anything? Could the system be grounded up to code in some way I am not thinking off? -Water main is grounded and seems to have its own electrode on other side of the house, but appears to not be directly bonded with any electrical.
Appreciate the help and happy new year.