GEC for parallel conductors

Merry Christmas

aelec84

Member
Location
Los Angeles
Occupation
Electrical Engineer
forum,

I have (2) parallel sets of 400kCMIL copper conductors and the GEC is connected to common ground bus and it is extending it to other electrodes. I believe equivalent area has to be considered which would be 800 kCMIL requiring 2/0 gec. Is this right? Thanks,
 
Per 2023 NEC, Table 250.66, Note 2 is confusing. What does that mean and when does it apply?
Note 2 is not applicable to your installation. If you had a sub-panel in a remote structure there would be no service conductors. In your scenario 2*400 kcmil=800 kcmil, from 250.66 that would be as you've stated correctly a #2/0 GEC.
 
Note 2 is not applicable to your installation. If you had a sub-panel in a remote structure there would be no service conductors. In your scenario 2*400 kcmil=800 kcmil, from 250.66 that would be as you've stated correctly a #2/0 GEC.
Thank you. To clarify these are not service-entrance conductors. The feeders are from separately derived system.
 