We are installing a 75kva 480/208Y120 transformer 300' from the Service Entrance Switchgear.
250.30(A)(3) Exception #2 allows the Grounding Electrode Conductor of a service to also be used for a Separately Derived System.
Normally we would run 3#2, 1#6G, and provide a Grounding Electrode at the transformer.
Using the above exception, would we run 3#2 phases, 1#6 EGC, plus 1#2 GEC?
Do we, somehow, need to identify the GEC differently from the EGC?
Do we even need the EGC if we promise not to cut/splice the GEC?
We'll probably do it the old way, but thought I'd see if anybody has done it this way.