acebradley
Member
- Location
- Colorado
I am looking at a specific installation where I am wondering if art. 250.30(A)(5) Exception 2 would apply. The installation in question is an MCC with a transformer and panel integral with the equipment. The transformer has a factory installed lug to accommodate a grounding conductor and the factory wired Neutral connection and factory installed jumper. There is no accommodation for a GEC for the separately derived ssystem grounding requirements. The feeders are hard piped all the way to the equipment. Would the grounding conductor ran with the feeders be considered a GEC if ? :
1. It is sized accordingly &
2. The conduit is considered to be the equipment ground &
3. The ground bus in the equipment is sized not smaller than the required GEC &
4. The equipment is listed and identified for use as service equipment
The MCC is European manufactured I believe. Some of the grounding terminals are labeled PEC
I have never dealt with something like this before, so I thought I would see if anyone else out there has.
1. It is sized accordingly &
2. The conduit is considered to be the equipment ground &
3. The ground bus in the equipment is sized not smaller than the required GEC &
4. The equipment is listed and identified for use as service equipment
The MCC is European manufactured I believe. Some of the grounding terminals are labeled PEC
I have never dealt with something like this before, so I thought I would see if anyone else out there has.