Sorry but this may be a long one. A 2 meter service upgrade. It has a metal underground water pipe. It has the sevice disconnects outside the house.
The electrician runs a gec from the water pipe to a ground bar in the first panel then to the ground bar in the second panel, to 2 ground rods outside.
I red tag because the gec connection is on the load side of the main disconnect, and the neutral is really not grounded.
Now here is the question. If the gec is removed from the ground rods and terminated in the main disconnect and the 2 groundrods are also terminated there, is the insallation code compliant?
250.62 (c) (3) seems to permit the gec to be connected to the ground bar.
The only thing that bothers me is that the egc and gec from the ser feeding the panels are in parallel. But there is no neutral to case connection made other than at the line side of the main disconnect. I asked the electrician why he did it that way. He said it was so there would still be a ground to the branch circuits if the egc failed. P.S the neutral and ground are isolated at the panels
The electrician runs a gec from the water pipe to a ground bar in the first panel then to the ground bar in the second panel, to 2 ground rods outside.
I red tag because the gec connection is on the load side of the main disconnect, and the neutral is really not grounded.
Now here is the question. If the gec is removed from the ground rods and terminated in the main disconnect and the 2 groundrods are also terminated there, is the insallation code compliant?
250.62 (c) (3) seems to permit the gec to be connected to the ground bar.
The only thing that bothers me is that the egc and gec from the ser feeding the panels are in parallel. But there is no neutral to case connection made other than at the line side of the main disconnect. I asked the electrician why he did it that way. He said it was so there would still be a ground to the branch circuits if the egc failed. P.S the neutral and ground are isolated at the panels