Chris Hunter
Member
Part 1: How does the NEC view the following with respect to service grounding. A multi Tenant building has 2 or more services. Building has steel reinforced concrete foundations and precast concrete exterior walls. Interior columns are steel on concrete footings on grade. Each service is 1600 amp 277/480 volt and each is served by 4 sets of 600kcmil cu THWN. Each service is served by a separate underground utility service lateral from separate pad mounted transformers. Service disconnects are 500 feet apart. One water service serves the building. The incoming underground water service is located 1000 feet from the nearest service and 1500 feet from the other service. Water pipe is bonded to the nearest column with 3/0 cu GEC is allowed to be connected at the service disc means to any point on the grounding electrode system. 3/0 cu GEC from each service is routed overhead to the nearest building steel joist(not to steel column. Steel joists and steel beams are bolted and/or welded together to form a continuous steel structure. Building is existing so the requirement for bonding the steel in the footing is removed . Does the installation comply with NEC requirements for service grounding?
Part 2: NEC recognizes a common GEC for multiple separately derived system and for multiple service enclosures grouped at one location served by a single service lateral. Is there any provision which would allow a 3/0 GEC to be routed from the water pipe to service one disconnect and then looped to service 2 disconnect for the services noted above. I find no provision which allow tapping these services to a common GEC
Part 2: NEC recognizes a common GEC for multiple separately derived system and for multiple service enclosures grouped at one location served by a single service lateral. Is there any provision which would allow a 3/0 GEC to be routed from the water pipe to service one disconnect and then looped to service 2 disconnect for the services noted above. I find no provision which allow tapping these services to a common GEC