It is fairly common in these parts for the E/Cs to use a 400 kcmil cu riser for a 400 amp residential service per 310.15(B)(6).
When they do so, they install a 1/0 GEC per 250.66
Today I had a job where the 400 amp service was fed by parallel 3/0 cu.
Per Table 8 3/0 is 167,800 x 2 = 335,600 which by 250.66 requires a #2 GEC.
When they do so, they install a 1/0 GEC per 250.66
Today I had a job where the 400 amp service was fed by parallel 3/0 cu.
Per Table 8 3/0 is 167,800 x 2 = 335,600 which by 250.66 requires a #2 GEC.