GEC out of transformer or panel

Status
Not open for further replies.

Mustang125

Member
Location
New Hampshire
Occupation
Master Electrician, Project Manager and Estimator
I cant seem to find in the code that the GEC must terminate with the bonding jumper. It would seem to me that as long as the supply side bonding jumper is sized the same as the GEC it should be code complaint. Am I missing something? See attachment
 

Attachments

  • xfomer GEC.pdf
    77.6 KB · Views: 17
250.30(A)(5) ..........This connection shall be made at the same point on the separately derived system where the system bonding jumper is connected.

Does that answer your question ?
 