M Mustang125 Member Location New Hampshire Occupation Master Electrician, Project Manager and Estimator Aug 11, 2021 #1 I cant seem to find in the code that the GEC must terminate with the bonding jumper. It would seem to me that as long as the supply side bonding jumper is sized the same as the GEC it should be code complaint. Am I missing something? See attachment Attachments xfomer GEC.pdf 77.6 KB · Views: 17
I cant seem to find in the code that the GEC must terminate with the bonding jumper. It would seem to me that as long as the supply side bonding jumper is sized the same as the GEC it should be code complaint. Am I missing something? See attachment
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 11, 2021 #2 250.30(A)(5) ..........This connection shall be made at the same point on the separately derived system where the system bonding jumper is connected. Does that answer your question ?
250.30(A)(5) ..........This connection shall be made at the same point on the separately derived system where the system bonding jumper is connected. Does that answer your question ?
M Mustang125 Member Location New Hampshire Occupation Master Electrician, Project Manager and Estimator Aug 11, 2021 #3 it sure does. doesn't get much more clear than that, cant believe I missed that... thank you