5-184 Log #450 NEC-P05 Final Action:
Reject
(250.64(B))
____________________________________________________________
Submitter: W. Creighton Schwan, Hayward, CA
Recommendation: Insert a new third sentence to read:
Where protection is provided by a raceway, it shall be RMC, IMC, RNC, or
EMT.
Substantiation: The last sentence prohibits the use of flexible metal conduit
for enclosing a grounding electrode conductor smaller than 6 AWG. This
makes sense, because current flow in a single conductor in a metal raceway is
approximately 90 percent on the raceway, 5 percent on the conductor. Flexible metal conduit is a relatively poor conductor due to the oil used in its
manufacture interrupting the turn-to-turn conductivity and resulting in a metal ribbon conductor three times the length of the raceway itself. This added sentence will make the rule the same for 4 AWG and larger as it is for 6AWG and smaller.
Panel Meeting Action: Reject
Panel Statement: The submitter has not provided technical substantiation that would restrict the current accepted use of listed bare armored conductors for use as grounding electrode conductors, which is a current common practice. There is no evidence provided that indicates there is a problem with these types of cables installed as grounding electrode conductors.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
This is ROP A2007