nyc dosent allow using one gec to bond multiple transformers,the building i'm working in has no building steel therefore i have to run separate gecs for three transformers,2 data racks and a fa fuse cutout(nyc) consisting of a #10,a #2,2#6s and 2#4s with a run length of approx 400ft.
 
Oh, I see, although who ever came up with this rule is, well......

I can't see any reason that you can't put them all in one conduit but I'm not in NYC either.