I have a service with 3 separate service disconnect switches rated 200amp each with 4/0 copper service entrance conductors tapped from 500MCM copper main service entrance conductors in a trough ahead of the switches.
My only grounding electrode for the building is a concrete-encased electrode.
Using the method allowed in 250.64(D)(1)(3) for my taps to a grounding busbar, I select #4 copper for my taps based on the 4/0 copper feeding each switch.
What size common ground electrode conductor is needed to the concrete-encased electrode from the grounding busbar is required?