I know that this subject has been beat to death but please bear with me.
In this part of the country we are stubbing out a piece of rebar through to floor in the basement or out of the top of the poured wall and then connecting a GEC to this stub out.
My question is this:
Can the GEC be smaller than #4 copper when the service entrance conductors are #1/0 copper and smaller and a rebar is stubbed out as mentioned above,250.66(B) says that it shall not be required to be larger than #4 copper but it does not say that you can use table 250.66 for GEC sizing when the service entrance conductors are smaller sizes,and the GEC is connected to a concrete encased rebar.
In other words can we use #6 copper connected to a 1/2 20' rebar encased in concrete.The rebar is the electrode and the wire is the GEC for a service that the service entrance conductors are #1 copper
In this part of the country we are stubbing out a piece of rebar through to floor in the basement or out of the top of the poured wall and then connecting a GEC to this stub out.
My question is this:
Can the GEC be smaller than #4 copper when the service entrance conductors are #1/0 copper and smaller and a rebar is stubbed out as mentioned above,250.66(B) says that it shall not be required to be larger than #4 copper but it does not say that you can use table 250.66 for GEC sizing when the service entrance conductors are smaller sizes,and the GEC is connected to a concrete encased rebar.