Re: GEC size
The maximum code required GEC is 3/0. This applies any time that you have over 1100 kcmil copper for the largest set of phase conductors. This would only apply to the GEC to the metal underground water pipe or the building steel. As others have pointed out, the code permits GECs smaller that shown in Table 250.66 for some electrodes.
Don