Hi all,
Let's say I have multiple grounding electrode conductor taps, originating from several service switches. All GEC taps terminate in a grounding bus bar. Then, from the grounding bus bar I have one GEC going to the cold water pipe, another GEC going to a ground rod, and a 3rd GEC going to building steel,
1. Can the GEC to the pipe be only a #6 AWG? Since after the pipe, the GEC doesn't extend further, I'm assuming that #6 is all that is needed, as opposed to fully sized.
2. Can the GEC to the ground rod also be sized for #6 AWG? For the same reason, since it doesn't extend further.
3. And the GEC to building steel would be fully sized, based on the size of the largest service entrance conductor.
Thanks for the help.
Let's say I have multiple grounding electrode conductor taps, originating from several service switches. All GEC taps terminate in a grounding bus bar. Then, from the grounding bus bar I have one GEC going to the cold water pipe, another GEC going to a ground rod, and a 3rd GEC going to building steel,