I have a 600 amp service that will have 4 individual service panels connected to it with each service having a 200 amp main disconnect. These will all be mounted below the C.T. adjacent to each other. This system will have service entrance condutors of 2 ea 500 mcm al. Table 250.66 tells me I need a 2/0 cu gec. Is it pemissible to run this from the ct can thru lay lugs in each panel in a continous fasion and then continue out to the gec electrode or do I have to bond it to each can and bring out a separate conductor from each to the g.e.?. I also assume that #4 cu is sufficient as an egc say from a bonding bushing at each raceway and then to the ground buss correct?