Greetings all
I am curious how precise you get with GEC sizing when a service is part or all bussbar ?
Say you have two service laterals from transformer bank to one service location on a commercial building.
Per 250.66 Note 1 we need to add up all the kCMIL of all the service conductors and size the GEC off the equivalent size:
There may be other situations where service conductors are busbar or combinations of wire and busbar.
Do you just look up the copper wire @75C that matches the busbar amps?
Or do you actually measure the busbar, convert square mills to circuilar mills?
Granted it probably does not often make a difference given the range of 250.66, but it might if you have a very long run of copper to do...
Or would some of you go off the utility demand sized laterals 350 Aluminum?
Or perhaps this is just too rare a situation.
I am curious how precise you get with GEC sizing when a service is part or all bussbar ?
Say you have two service laterals from transformer bank to one service location on a commercial building.
- First lateral lands on a 400A bus bar (meter mod with three 200A tenant meters).
- Second goes to a 400A CT can that will have two 200A disconnects tapped off it fed with 3/0 CU.
Per 250.66 Note 1 we need to add up all the kCMIL of all the service conductors and size the GEC off the equivalent size:
1. If multiple sets of service-entrance conductors connect directly to a
service drop, set of overhead service conductors, set of underground
service conductors, or service lateral, the equivalent size of the largest
service-entrance conductor shall be determined by the largest sum of
the areas of the corresponding conductors of each set.
There may be other situations where service conductors are busbar or combinations of wire and busbar.
Do you just look up the copper wire @75C that matches the busbar amps?
Or do you actually measure the busbar, convert square mills to circuilar mills?
Granted it probably does not often make a difference given the range of 250.66, but it might if you have a very long run of copper to do...
Or would some of you go off the utility demand sized laterals 350 Aluminum?
Or perhaps this is just too rare a situation.