This is a strange apartment building. It is 1 building that has 3 overhead lines from the power company. Each of those lines is getting double tapped and feeding 2/0 SEU (aluminum) down to a group of meters.
The GEC has been sized according to 250.66 with 2/0 aluminum as the largest ungrounded conductor.. Which would make it a #6 CU GEC.
Inspector is saying sense each drop is tapped with qty. 2 - 2/0 SEU then the GEC should be sized for the equivalent area of qty. 2 - 2/0 AL. (or even larger as what will be discussed below.)
According to table 8, 2/0 is 67.43mm x2 = 134.86mm, making the equivalent conductor size 300kcm, requiring a GEC of #2 copper (or 1/0AL)
The answer should be in 250.64 (d)(1).
Typically I would be disagreeing with the inspector because to me it says size the GEC according to the largest conductor feeding the disconnect.
But my confusion is, there is already is an existing GEC ran. The existing GEC is 1 single unbroken #6cu from the water main and it is lugged onto each panel. As in this #6 is attached to possibly 12 panels.
Hopefully this crude drawing helps with understanding.
The GEC has been sized according to 250.66 with 2/0 aluminum as the largest ungrounded conductor.. Which would make it a #6 CU GEC.
Inspector is saying sense each drop is tapped with qty. 2 - 2/0 SEU then the GEC should be sized for the equivalent area of qty. 2 - 2/0 AL. (or even larger as what will be discussed below.)
According to table 8, 2/0 is 67.43mm x2 = 134.86mm, making the equivalent conductor size 300kcm, requiring a GEC of #2 copper (or 1/0AL)
The answer should be in 250.64 (d)(1).
Typically I would be disagreeing with the inspector because to me it says size the GEC according to the largest conductor feeding the disconnect.
But my confusion is, there is already is an existing GEC ran. The existing GEC is 1 single unbroken #6cu from the water main and it is lugged onto each panel. As in this #6 is attached to possibly 12 panels.
Hopefully this crude drawing helps with understanding.