My question has to do with the sizing of the grounding electrode conductor, and what is the grounding electrode conductor in my situation. There may be other items spur off from this question.
The service is 4,000 Amp, 208V, 3 Phase using 11 - 500 kcmil CU per phase.
I called for three electrodes from 250.52(A): 1) Water pipe, 2) a concreete encased electrode of 4 AWG Cu, and 3) a counterpoise electrode consisting of 3 10', 3/4", driven ground rods in a triangular arrangement.
If I require all of these to be tied directly back to the neutral bus, then what is the GEC that needs to be sized per table 250.66?
From 250.66(A) the electrode conductor from the ground rods to the busbar are not requied to be large than #6 AWG Cu; 250.66(B) only requies a #4 Cu from the concrete encased electrode. Is there any place that the code specifies the size of the electrode conductor to the water pipe? The size of these conductors just don't seem to be substantial enough for a system of this size.
I believe the bonding jumper between the ground bus and the neutral bus will be required to be sized per 250.66.
I have read many useful comments on different threads, but have not seen my specific questions answered. I would appreciate all the help I can get.
The service is 4,000 Amp, 208V, 3 Phase using 11 - 500 kcmil CU per phase.
I called for three electrodes from 250.52(A): 1) Water pipe, 2) a concreete encased electrode of 4 AWG Cu, and 3) a counterpoise electrode consisting of 3 10', 3/4", driven ground rods in a triangular arrangement.
If I require all of these to be tied directly back to the neutral bus, then what is the GEC that needs to be sized per table 250.66?
From 250.66(A) the electrode conductor from the ground rods to the busbar are not requied to be large than #6 AWG Cu; 250.66(B) only requies a #4 Cu from the concrete encased electrode. Is there any place that the code specifies the size of the electrode conductor to the water pipe? The size of these conductors just don't seem to be substantial enough for a system of this size.
I believe the bonding jumper between the ground bus and the neutral bus will be required to be sized per 250.66.
I have read many useful comments on different threads, but have not seen my specific questions answered. I would appreciate all the help I can get.