I'm going to take a stab at it, since I had an inspector point it out to me. Not all crimps, lugs, etc are grounding and bonding rated. The YGS8C is.
 

kwired

Electron manager
Location
NE Nebraska
I'm going to take a stab at it, since I had an inspector point it out to me. Not all crimps, lugs, etc are grounding and bonding rated. The YGS8C is.

I would have taken pretty much the same stab at it. I did not look it up but am pretty certain the catalog number with the "G" in it is the one rated for grounding. It also likely recommends a different crimping tool than the other model, I think that is true for most all connectors rated for grounding, I think they compress at a higher pressure level.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I would have taken pretty much the same stab at it. I did not look it up but am pretty certain the catalog number with the "G" in it is the one rated for grounding. It also likely recommends a different crimping tool than the other model, I think that is true for most all connectors rated for grounding, I think they compress at a higher pressure level.

I just wonder why would grounding need to have a higher pressure level than any other splice?
 

sandsnow

Senior Member
There are two cases I found where the connection has to be made with a device listed for grounding and bonding. The splicing of the GEC and the Intersystem Bonding terminal 250.94.

Everything else has the option of using simply Listed devices. Even the where a ground bus (to connect bonding jumpers to) in 250.64(F) just requires listed connector.

Doesn't seem to make sense.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
There are two cases I found where the connection has to be made with a device listed for grounding and bonding. The splicing of the GEC and the Intersystem Bonding terminal 250.94.

Everything else has the option of using simply Listed devices. Even the where a ground bus (to connect bonding jumpers to) in 250.64(F) just requires listed connector.

Doesn't seem to make sense.

You can say that again. I guess I need to start looking for the correct tools and materials.
 

gndrod

Senior Member
Location
Ca and Wa
Burndy

Burndy

What is the difference between a Brundy YS8C and a YGS8C crimp as it relates to splicing a GEC, indoors?

Hi Norb,

It's been a while, but your question needs a simple answer. Burndy has been around as long as I remember when installing rack and panel equipment in the 50's. The difference has a two-fold answer....that YS8C is either an 8 Awg Cu-tin plated inline splice HYLINK crimp barrel or HYLUG one hole crimp copper tin-plated 8 Awg lug.

The YGS8C is a HYGROUND 8 Awg compression terminal of various configurations that are used to bond a cross-grid system together in a foundation (rebar cross-grid) or direct buried configuration such as used in radio tower ground ring splices. I would say that the old technology has disappeared for bonding Cu direct burial rays from a ring, but the cross-grid rebar or shield grid bonding in structures is very common. I hope this helps. rbj
 