Consider an outdoor service disconnect bottom fed by a PVC conduit exiting the ground. Can a #6 GEC leaving the enclosure and going into the gorund be strapped to the conduit? Here is the wording of 300.11(B) (assume none of the conditions are met).
Is a GEC a "cable"? I guess it comes down to whether they mean cable as in "cable assembly" or just a loose definition. I lean toward a GEC is not a cable and thus allowed.
Raceways Used as Means of Support. Raceways
shall be used only as a means of support for other raceways,
cables, or nonelectrical equipment under any of the
following conditions:
Is a GEC a "cable"? I guess it comes down to whether they mean cable as in "cable assembly" or just a loose definition. I lean toward a GEC is not a cable and thus allowed.