R rogue6144 Member Jun 24, 2013 #1 Can a dual rated tap connector be used to connect a #6 cu GEC tap condutor to a 250mcm Al common GEC? Not a split bolt, a lay in type lug. None of the lugs I've looked at say anything about grounding or bonding. Thanks, Rogue6144
Can a dual rated tap connector be used to connect a #6 cu GEC tap condutor to a 250mcm Al common GEC? Not a split bolt, a lay in type lug. None of the lugs I've looked at say anything about grounding or bonding. Thanks, Rogue6144
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 24, 2013 #2 250.64(D)(1)(1) requires the connector to be listed for grounding and bonding.