GEC termination location

Status
Not open for further replies.

olly

Senior Member
Location
Berthoud, Colorado
Occupation
Master Electrician
I got a two part question:

  1. Can you run a bare #6 GEC (waterpipe ground) through the same conduit that feeders are running through to get to the main disconnect. I thought I heard you cannot do this.
  2. Can the termination point of a waterpipe ground and G-rod bare #6 land under the intersystem bonding device and then just have one #6 go from the intersystem bonding device to the main disconnect? Or does each GEC need to land in the main disconnect and then drop one #6 to the intersystem boding device?
 
Is the 6 AWG solid or stranded?
No on question #2
There is one GEC, unspliced to the service disconnect. To other electrodes those are bonding jumpers and can connect for example, to water pipe where the GEC ends
 