Can anyone explain why it's not allowed to use an intersystem bond bar for the GECs from a multi meter /multi disconnect service ?
Can anyone explain why it's not allowed to use an intersystem bond bar for the GECs from a multi meter /multi disconnect service ?
You have to use one of the methods and/or clamps listed in 250.
The innersystem bridge is not listed there nor is it listed by a NTL for that purpose.
These are the legal reasons, from a practicable standpoint I don't see a problem.
You can use it for the GEC's required in certain Chapter 7 & 8 applications. It is basically for interconnecting and terminating grounding conductors from telephone, CATV, radio and TV antennas. See 250.94. An intersystem bond bar is not intended for use within the grounding electrode system required under Article 250 Part III.Can anyone explain why it's not allowed to use an intersystem bond bar for the GECs from a multi meter /multi disconnect service ?
"This way" is fine if it is appropriately sized bus bar. Listed intersystem bond bars are too small.In nyc when i do a service that consists of more then one panel, disconnects, meters etc they perfer it done this way all the bonds connected to a copper ground bar along with the ground rod and water main
okay... just that you gotta be specific here or someone like me will pick your post to pieces...We dont use an intersystem bond bar for all the bonds what i ment is we use a copper isolated ground bar typically seen in data rooms the intersystem bond bar is only used for tv and cable providers so they don't use our svc mast as a ground its a local code here