Hello,
The GEC can terminate on the incoming service line neutral, in the meter can neutral, or at the main service disconnect neutral.
The MBJ must be at the incoming service neutral to bond the neutral to the case/ EGC bar.
The GEC CAN land on the grounding bar terminal bar if there is a wire type or buss bar type MBJ connecting to the neutral bar where the service neutral lands.
Question: Why is it so important the GEC land on the neutral bar? The GEC and the ground electrodes are really only used for reducing insulation stress from built up voltage/charge from over voltages, lightning, load switching etc. The MBJ is the main tool that does the clearing of faults. If all equipment is properly bonded, and there is a line to case fault, the fault current travels through the mental enclosure to the EGC, back to the service disconnect, hitchhikes a ride on the MBJ to the neutral and sent back to the source to clear the fault. The GEC and the ground electrodes play no role in this, so why is it important for the GEC to land on the neutral?
Is it because there is where it is doing its charge reduction magic - at the neutral?
The GEC can terminate on the incoming service line neutral, in the meter can neutral, or at the main service disconnect neutral.
The MBJ must be at the incoming service neutral to bond the neutral to the case/ EGC bar.
The GEC CAN land on the grounding bar terminal bar if there is a wire type or buss bar type MBJ connecting to the neutral bar where the service neutral lands.
Question: Why is it so important the GEC land on the neutral bar? The GEC and the ground electrodes are really only used for reducing insulation stress from built up voltage/charge from over voltages, lightning, load switching etc. The MBJ is the main tool that does the clearing of faults. If all equipment is properly bonded, and there is a line to case fault, the fault current travels through the mental enclosure to the EGC, back to the service disconnect, hitchhikes a ride on the MBJ to the neutral and sent back to the source to clear the fault. The GEC and the ground electrodes play no role in this, so why is it important for the GEC to land on the neutral?
Is it because there is where it is doing its charge reduction magic - at the neutral?