Just came from a job where a GEC was clamped to the water pipe close to the water entrance point and then continued out to the service disconnect and ground rod outside.
Since there was neutral current on the pipe due to an incorrect connection from the subpanel neutral bus, I had current to measure. The neutral current flowed on the pipe to where the clamp connected with the GEC which went out to the service disconnect outside.
With a clamp-on I measured the current, which went from the panel and on the pipe to the GEC and then out on the GEC to the meter box. None of it continued out on the water pipe. From this I conclude that the town water service is plastic. So I would have the GEC from the meter box outside just go to the nearest pipe (bonding) instead of within 5' of the water entrance, since I conclude there is no water pipe grounding electrode.
But would an inspector need to visually see the plastic entrance pipe?
Karl
Since there was neutral current on the pipe due to an incorrect connection from the subpanel neutral bus, I had current to measure. The neutral current flowed on the pipe to where the clamp connected with the GEC which went out to the service disconnect outside.
With a clamp-on I measured the current, which went from the panel and on the pipe to the GEC and then out on the GEC to the meter box. None of it continued out on the water pipe. From this I conclude that the town water service is plastic. So I would have the GEC from the meter box outside just go to the nearest pipe (bonding) instead of within 5' of the water entrance, since I conclude there is no water pipe grounding electrode.
But would an inspector need to visually see the plastic entrance pipe?