While performing a grounding and bonding inspection at a customer facility, I found a properly sized GEC connected between the main ground bus and the water main within 5' of where the water enters the building.
The problem I'm struggling with is routing of the GEC. It exits the main service equipment panel in one conduit of a parallel circuit (two conduits) to a feeder panel. It is not terminated in the feeder panel and exits it through a dedicated conduit to the water main located in another room.
Does this violate any part of NEC250? I have been unable to find anything that would prohibit this routing, but my gut tells me this could be done better. It seems that if the conduit and the feeder panel are appropriately bonded this is an acceptable path for the GEC.
Any insight?