250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment
grounding conductors shall be permitted to be bare,
covered, or insulated. Individually covered or insulated
equipment grounding conductors shall have a continuous
outer finish that is either green or green with one or more
yellow stripes except as permitted in this section. Conductors
with insulation or individual covering that is green,
green with one or more yellow stripes, or otherwise identified
as permitted by this section shall not be used for ungrounded
or grounded circuit conductors.
Exception No. 1: Power-limited Class 2 or Class 3 cables,
power-limited fire alarm cables, or communications cables
containing only circuits operating at less than 50 volts
where connected to equipment not required to be grounded in
accordance with 250.112(I) shall be permitted to use a conductor
with green insulation or green with one or more yellow
stripes for other than equipment grounding purposes.
Exception No. 2: Flexible cords having an integral insulation
and jacket without an equipment grounding conductor
shall be permitted to have a continuous outer finish that is
green.
Informational Note: An example of a flexible cord with
integral-type insulation is Type SPT-2, 2 conductor.
Exception No. 3: Conductors with green insulation shall be
permitted to be used as ungrounded signal conductors
where installed between the output terminations of traffıc
signal control and traffıc signal indicating heads. Signaling
circuits installed in accordance with this exception shall
include an equipment grounding conductor in accordance
with 250.118. Wire-type equipment grounding conductors
shall be bare or have insulation or covering that is green
with one or more yellow stripes.