GEC

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
On a sub feed panel to a out building 4 wire 120/240 single phase do you connect the GEC to the neutral bar or the grounding bar.
 
The ground bar, the neutral is isolated from the metallic parts of the system in a sub-panel in a separate structure.
 