I have reason to believe the engineers I work with are sizing the Grounding Electrode Conductors (GEC) wrong. Please inform me if I am not doing this correct. This is not everything on the print will be here forever but heres partial as seen below:
800A 3Phase 480V MDP (2) parallel 500kcmil, Feeds 400A, 3Phase, 480v HP1, Feeds 75kVA xfmr, Which Feeds 200A, 3Phase, 120/208V LP1.
GEC Common 2/0 Main GEC from MDP to ground box 1 (GB1) with groundbar per NEC. tapped with 1/0 GEC from HP1 back to GB1, tapped with #6 GEC from xfmr back to GB1, tapped with #4 GEC from LP1 back to GB1, tapped with #6 GEC from Anode to GB1, tapped with 2/0 GEC from building steel to GB1. (23) groundboxes throught the facility basically done the same way.
My questions are: when multi tapping to the equipment the GEC has to be the sized per the largest conductor in the equipment.
Sorry for any troubles understanding easier to show one-line. Please let me know
800A 3Phase 480V MDP (2) parallel 500kcmil, Feeds 400A, 3Phase, 480v HP1, Feeds 75kVA xfmr, Which Feeds 200A, 3Phase, 120/208V LP1.
GEC Common 2/0 Main GEC from MDP to ground box 1 (GB1) with groundbar per NEC. tapped with 1/0 GEC from HP1 back to GB1, tapped with #6 GEC from xfmr back to GB1, tapped with #4 GEC from LP1 back to GB1, tapped with #6 GEC from Anode to GB1, tapped with 2/0 GEC from building steel to GB1. (23) groundboxes throught the facility basically done the same way.
My questions are: when multi tapping to the equipment the GEC has to be the sized per the largest conductor in the equipment.
Sorry for any troubles understanding easier to show one-line. Please let me know