C codequestion Banned Location MD, USA Mar 28, 2018 #1 Can you install bare copper GEC in PVC or does the GEC hae to be insulated? Sent from my SM-G935U using Tapatalk
Can you install bare copper GEC in PVC or does the GEC hae to be insulated? Sent from my SM-G935U using Tapatalk
Ponchik Senior Member Location CA Occupation Electronologist Mar 28, 2018 #2 Bare is OK. Did someone give you a code reference that you can not?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 28, 2018 #3 See 250.62