Put in a new service with GEC run to 2 rods no ufer available tied to service panel in basement of home.
Power company hooks up service.
After they're done I see they put another ground wire in from meter base to my GEC connected with a split bolt.
OK so now I'm thinking they just created a parallel neutral between meter box and service panel by doing so.
Knowing this is not allowed what should I do? Remove my GEC from panel or just go on without incident or start contacting these power companies to stop the requirement to install the GEC at the meter box only and allow to be connected per NEC at any of the 3 locations it can attach to. Once and done.
We have 3 main power companies around my area with even a few more co-ops operating around, naturally having different requirements as to whether they want a ground installed in the meter base or not.
Some while ago I had one of there installation requirement papers show to run ground to there meter base and electrician to run another ground to the service panel which looked like wording added to an existing paper that used to just say "to the meter base"
So are they in the wrong by having said this?
Do they really have a say on anything that happens on the load side of a meter base? The way I see it the demarcation is the line side terminals of meterbase. From then on the NEC takes effect.
The bad and ugly, would be if my neutral terminations should go bad between meterbase and panel then current flow would be on their ground wire and by that time a corroded connection that could lead to high temperatures at the joint which could cause fire.
Power company hooks up service.
After they're done I see they put another ground wire in from meter base to my GEC connected with a split bolt.
OK so now I'm thinking they just created a parallel neutral between meter box and service panel by doing so.
Knowing this is not allowed what should I do? Remove my GEC from panel or just go on without incident or start contacting these power companies to stop the requirement to install the GEC at the meter box only and allow to be connected per NEC at any of the 3 locations it can attach to. Once and done.
We have 3 main power companies around my area with even a few more co-ops operating around, naturally having different requirements as to whether they want a ground installed in the meter base or not.
Some while ago I had one of there installation requirement papers show to run ground to there meter base and electrician to run another ground to the service panel which looked like wording added to an existing paper that used to just say "to the meter base"
So are they in the wrong by having said this?
Do they really have a say on anything that happens on the load side of a meter base? The way I see it the demarcation is the line side terminals of meterbase. From then on the NEC takes effect.
The bad and ugly, would be if my neutral terminations should go bad between meterbase and panel then current flow would be on their ground wire and by that time a corroded connection that could lead to high temperatures at the joint which could cause fire.