tryinghard
Senior Member
- Location
- California
In my scenario below structures 1-2 include #8cu GEC/bonding jumpers based on feeder size; these aren?t required to be larger are they (I don?t see it if so)?
Electrodes at structure 1 = 1600A service disconnect (SWG) with GEC/bonding jumper:
1- CEE, 3/0 cu
2- Metal frame, 3/0 cu
3- Rods, 6 cu
Electrodes at structure 2 = 125A feeder (#2's) with GEC/bonding jumper:
1- CEE, 8 cu
2- Metal frame, 8 cu
Electrodes at structure 3 = 80A feeder (#4's) with GEC/bonding jumper:
1- CEE, 8 cu
2- Metal frame, 8 cu
In keeping with:
250.32.B (sized per 250.122 for grounding or bonding of equipment, structures, frames?required)
250.50 (related electrodes connected that are served ? not fed)
250.53.C
250.66
Electrodes at structure 1 = 1600A service disconnect (SWG) with GEC/bonding jumper:
1- CEE, 3/0 cu
2- Metal frame, 3/0 cu
3- Rods, 6 cu
Electrodes at structure 2 = 125A feeder (#2's) with GEC/bonding jumper:
1- CEE, 8 cu
2- Metal frame, 8 cu
Electrodes at structure 3 = 80A feeder (#4's) with GEC/bonding jumper:
1- CEE, 8 cu
2- Metal frame, 8 cu
In keeping with:
250.32.B (sized per 250.122 for grounding or bonding of equipment, structures, frames?required)
250.50 (related electrodes connected that are served ? not fed)
250.53.C
250.66