We've discussed this before but due to the fact I'll be installing a couple of these in the near future I'd like to confirm my thoughts. The 8 circuit generator panel in question will be a panel with a factory installed interlock, along with a 60a dbl pole, this is not a prewired assembly. I am/was planning on wiring it in the same manner seen in post #8 by electricmanscott in this thread:
http://forums.mikeholt.com/showthread.php?t=121224&p=1143799#post1143799
Meaning, I would not relocate the branch circuit neutrals nor their egc's to the gen panel. Thus, a 24" or less nipple connecting the main panel to gen panel would contain the following: two #6 ungrounded conductors, #10 egc, #10 neutral, and up to eight #12's for the bc's. Now this is how I'd LIKE to wire it, however, if I understand previous threads, this would fly if it were a prewired assembly but since I would wire it myself, the raceway/nipple must contain all the bc grounded conductors (And egc's?) therefore the main panel would serve only as a j-box for said conductors in this case. I'd have to go up to a #6 neutral if I had to go this route.
http://forums.mikeholt.com/showthread.php?t=121224&p=1143799#post1143799
Meaning, I would not relocate the branch circuit neutrals nor their egc's to the gen panel. Thus, a 24" or less nipple connecting the main panel to gen panel would contain the following: two #6 ungrounded conductors, #10 egc, #10 neutral, and up to eight #12's for the bc's. Now this is how I'd LIKE to wire it, however, if I understand previous threads, this would fly if it were a prewired assembly but since I would wire it myself, the raceway/nipple must contain all the bc grounded conductors (And egc's?) therefore the main panel would serve only as a j-box for said conductors in this case. I'd have to go up to a #6 neutral if I had to go this route.
Last edited by a moderator: