I found an old thread (2013) that was closed on this which helped a little but thought I would bring it up for discussion.
From my research of NFPA20 due to the by-pass handle required per NFPA20 10.5.3.2 on the controller the generator needs to be size for across the line starting. NFPA20 9.6.5 has explanatory paragraph A.9.6.5 which specifically states this. See attached snip
When you have a 200HP fire pump that is not going to be a small generator. One of those worst case scenarios we need to plan for that would only happen if we did not. We've all been there.
I understand the 15%VD requirement of NFPA20 9.4.1 does not apply when in manual bypass per 9.4.2 & 9.4.3 but you still need to demonstrate the gen set can start with the fire pump and any additional load it carries. 'Ignoring' the 15% VD is nice but in the end it will really help a whole lot. Ill be looking to work with a supplier to size it but wanted to see if anyone had any comments on this.
IMO this requirement really sells the use of a diesel FP for those large HP pumps unless you can meet the NFPA requirements of a reliable source of power and get the AHJ to agree. Something I have done only 2 times in my 25 plus years doing this.
Thanks for the replies!
From my research of NFPA20 due to the by-pass handle required per NFPA20 10.5.3.2 on the controller the generator needs to be size for across the line starting. NFPA20 9.6.5 has explanatory paragraph A.9.6.5 which specifically states this. See attached snip
When you have a 200HP fire pump that is not going to be a small generator. One of those worst case scenarios we need to plan for that would only happen if we did not. We've all been there.
I understand the 15%VD requirement of NFPA20 9.4.1 does not apply when in manual bypass per 9.4.2 & 9.4.3 but you still need to demonstrate the gen set can start with the fire pump and any additional load it carries. 'Ignoring' the 15% VD is nice but in the end it will really help a whole lot. Ill be looking to work with a supplier to size it but wanted to see if anyone had any comments on this.
IMO this requirement really sells the use of a diesel FP for those large HP pumps unless you can meet the NFPA requirements of a reliable source of power and get the AHJ to agree. Something I have done only 2 times in my 25 plus years doing this.