Hi ,
one of my customer needs to know which emergency back up system is less expensive for the new in-coming tenant operating as private surgon with a surgery room in that buldg.
also note that, there is no room extra available in the bldg but plenty of parking areas.
Generator set or batteries ?????
Do you know who is the good provider or manufactorer for battery / UPS system??
Tanx
There are many options to consider.
The total and projected critical load!
Is the property leased or owned?
If leased, you have many more issues to consider prior to a Gen set!
Noting your statement of no space in the property, is that regarding the potential use of a Gen set or just installing a UPS battery backup within the property?
Either way, your expansion issues include, 24 hour cooling for UPS system.
Use a Gen set, then you have other Tennant concerns. Engineering for that could be very expensive if allowed by the property owners.
Then you have cooling fin spacing on your genset radiator, if your planning on adding life safety for the entire property or just one Tennant. The specs on the generators will tell you if it is rated for Industrial or Commercial Business Park use. The DBA' rating would have to be low enough to not bother other owners and Tennant's in the same community. And or if your near residential homes or not?
If fixed load is known, then, I would consider a modular UPS, i.e. AC or others, find the space for cooling and storage, ensure that your only using sealed no maintenance batteries.
If Owned, and your future clients could be the same type of end users, then, I would look at a long term plan to include the ability to expand, with no intiruption to current or future client loads.
Obviously, a smaller UPS would heal the wound, but not serve the long term goal.
Correct planning and budgeting is obviously a great tax tool with respect to installing UPS and or Genset, as spare parts for both can be included in or added to the Capex or business expense, adding not only installed as is, but maintaining spare parts as well.
This would reduce the operating expense to the client when something goes wrong and ensure 100% uptime for client. If that's what you or the client are considering!