ptonsparky
Tom
- Occupation
- EC - retired
Generator, optional.
Customer with 400 amp and (new) 600 amp manual transfer switches. SE rated. We were originally going to limit the load to essential use and feed both with the small genset used for the 400. Customer comes home with a 1200 amp genset he bought on an auction. It will be sitting outside under a large carport. Not a SDS. The calculated load is around 750. We used 3 sets of 350 Al for a feed from the utility. What size do I need to use from the new genset? Equal to my 350s? The 1000 amp to a gutter and tap off from there? Or the 1200?
Customer with 400 amp and (new) 600 amp manual transfer switches. SE rated. We were originally going to limit the load to essential use and feed both with the small genset used for the 400. Customer comes home with a 1200 amp genset he bought on an auction. It will be sitting outside under a large carport. Not a SDS. The calculated load is around 750. We used 3 sets of 350 Al for a feed from the utility. What size do I need to use from the new genset? Equal to my 350s? The 1000 amp to a gutter and tap off from there? Or the 1200?