horrorsix
Member
- Location
- Harrisburg PA
I have a residential customer with with about 100' run from the location generator to the transfer switch and panel location. Would it be OK to run aluminum wire or should it be copper?
Generac's breakers and ATS are rated for copper. They are not duel rated.
I bet you'd still be way ahead to run aluminum and use insulated taps for pigtailing to copper.
There is no doubt. I bought 125ft 3/0 Cu last week $ 3.98 per ft.:jawdrop:
Where does it say that CEB? I'm looking at my transfer switch manual and it states that if you are using aluminum wire be sure to use a corrosion inhibitor. If they start producing these units made for copper only we're in deep $=!+. BTW, that little copper ground bar at the bottom left corner of the xfer switch is not rated for aluminum wire (if that's what you were referring to ).Generac's breakers and ATS are rated for copper. They are not duel rated.
Where does it say that CEB? I'm looking at my transfer switch manual and it states that if you are using aluminum wire be sure to use a corrosion inhibitor. If they start producing these units made for copper only we're in deep $=!+. BTW, that little copper ground bar at the bottom left corner of the xfer switch is not rated for aluminum wire (if that's what you were referring to ).