Generac 7.5KW PowerPact ATS Neutrals
ciscojoe
Boston
Engineer
In reference to a Generac 7.5 KW PowerPact generator. It ships with Automatic Transfer Switch (2 Pole). Reviewed ATS installation documentation. I believe install documentation contradicts itself. This is a 2 pole ATS, so Neutral is not switched. Factory installation Manual instructions say connect Main panel Neutral to ATS Neutral. Connect Generator Neutral to ATS Neutral. Then remove all targeted backup circuit neutrals, from Main Panel Neutral, and connect to ATS Neutral Bus. This makes no sense to me. Why not just leave targeted circuit Neutrals on Main Neutral Bus?
I should add, the in question (Model 0K7618B) ATS is not a whole house unit but one of Generac's 10 circuit sub panel variants, which ships with Generator (Model G0069981). So, 10 circuits would be abandoned in Main Panel and wired into ATS panel, which hosts breakers, hence my moving the Neutrals reference!
The older models used a large neutral in the factory whip, so the circuit neutrals remained in the main panel. Now due to the advent of arc fault protection, the neutrals have to be moved to the Generac loadcenter.
hillbilly1, thanks for the reply, it is appreciated!! This particular ATS does not ship with any pre wiring, hence no factory whip. Install consists of installing a 50 amp breaker, in main panel. Extending two #6's from said breaker to Utility side of ATS (switched), extending similar ground from main panel to ATs unswitched ground, and extending a #6 from the Main panel neutral, to the ATS unswitched Neutral. So, this results in the Neutral in the main panel and at ATS panel being cross connected, all the time. With that being said, what does moving the neutral from the targeted circuits being backed up, to the ATS Neutral provide? From an engineering perspective it is now one bus (Main Neutral cross connected to unswitched ATS Neutral). This is what I am having trouble understanding. It is just some addition wire work, with little cost to do so, but I cannot simply understand the reasoning. I find nothing in NEC, or anywhere else, the makes me understand this.
There is a rule that the neutrals are supposed to originate in the same panel as the hots.
The older manual multi-circuit T/Ss with the whips did not require relocating the neutrals.
Generac had those prewired whips for their automatic transferswitches too. They had a large neutral with the rest being hots, two hots to feed the switch, then a bunch of #12’s, and a couple of #10’s off the breakers in the t’switch loadcenter.
I now have an additional NEC question, that is fostering opposing opinions from the supply house counter electricians.
My well pump died (installed 26 years ago by people unknown). 1.5 HP, 25 GPM 2 wire, with ground (#10 solid).
Opened well cap and see at top of 6 inch well casing a 2 lug grounding block connected to well casing. Ground from pump connects to one lug, ground from service connects to 2nd lug.
Much debate as to if this meets code, or is even required!!
Opinion?
What kind of engineer are you? Are you an electrician also?
The Home Depot counter is not the place to get electrical advice. Maybe call an electrician to help you with these issues. 👍
I am an Electrical Engineer, and the Suply house is Baynes Electric, were local electricians congregate when picking up stock, and there was no general consensus as to the grounding of said 21 wire pump
I would want the well casing bonded to the EGC myself.
If the wiring to the pump got skinned on the metal well casing, with out the EGC connected to it, it would simply energize the casing and not clear the fault.
Jap>
It's generally the misconception that since the well casing is buried so deep in the dirt that it will clear a fault without an EGC bonded to it.
Relying on that to happen in any electrical installation is just bad practice in my book.
Jap>