Generac control wiring

Status
Not open for further replies.

Gushud

Member
Location
Massachusetts
Does the control wiring have to be in a different conduit as the feeder conductors coming from the generator to the transfer switch if the control conductors are rated 600v


Sent from my iPhone using Tapatalk
 

Seekthetruth

Member
Location
Florida
Occupation
Electrical
Can you hook up an automatic transfer (stationary generator) switch with a manual switch which goes to a portable generator to feed the same load?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Does the control wiring have to be in a different conduit as the feeder conductors coming from the generator to the transfer switch if the control conductors are rated 600v
It depends on the manufacturer's instructions. Generac used to supply whips on their units that contained all of the wires, then instructed us to run separate conduits. Now they supply no whips, and we can run them all in a single conduit.

I will use whichever method suits the installation. Sometimes, like through a crawlspace, I'll use SER for the feeder and a separate 1/2" LFNC for the control wires. Other times, , like a surface run, I'l use a single PVC conduit and single wires.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Can you hook up an automatic transfer (stationary generator) switch with a manual switch which goes to a portable generator to feed the same load?
Probably need to start another thread, but I’m assuming you are wanting to install an automatic switch, but use it with a portable non-automatic generator?
 

sparky1118

Senior Member
Location
Massachusetts
Occupation
Master Electrician
Does the control wiring have to be in a different conduit as the feeder conductors coming from the generator to the transfer switch if the control conductors are rated 600v


Sent from my iPhone using Tapatalk

No they don’t. Just get the generator cable that has all the wires already bundled together it’s direct burial. One cable does it all


Sent from my iPhone using Tapatalk Pro
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
No they don’t. Just get the generator cable that has all the wires already bundled together it’s direct burial. One cable does it all


Sent from my iPhone using Tapatalk Pro
Cablemaster mfg one for generac that is all in one cable for up to 22kw.
1601463663619.png
 